tbran
Guest
I doubt the recharge oil is your problem. The only way to really diagnose your problem is with a set of gauges. See what the pressures are. High side should be about 150PSI PlUS the outside temp. Thus 200-275 range. low side should be 10-18PSI. Slightly high low pressure usually indicates moisture and high low perssure indicates faulty expantion valve. Inability to obtain high pressure indicates either a faulty expantion valve or rarely a faulty compressor. MAny compressors are unnecessarily replaced. It is imperitive to pull a good vacuum for at least 30 minutes. lowering the pressure to 28-29 inches of vacuum lowers the boiling point of water so as it is exhasted as vapor and thus leaving the system free of H20 which prevents the freon doing its job. NORMAllY 3.5 small cans will fill the system but we use pressures instead of weight to charge systems. Again follow the first set of pressures given to charge the system. It is very easy to overcharge R134a be carefull as too much is worse than not enough. let me add we have picked up R12 replacement from NAPA - I think it is Freeze12IJ - and it works great. Some of the propaganda about replacements are not true. I feel if a nationwide chain like NAPA endorses and sells a product for a few years it must be safe to use. Finally we also use a can of stop leak in all old systems